Три причины по oPE18 возможны:
1. S3-29 and S3-30 are set to the same value, meaning that the input from load cell with load condition 1 (S3-29) is set to the same value as load condition 2 (S3-30). Correct the values set to S3-29 and S3-30.
2. The Dwell 2 speed reference in S3-20 is greater than 0.00 but is still less than the Dwell 2 End Speed in S3-21. Correct the values set to S3-20 and S3-21.
3. Open Loop Vector Control is selected (A1-02 = 2), Online Tuning is enabled (n6-01 = 2), and
one of the following contradictory settings exists:
• E2-02 is set to 30% or less of its factory default.
• E2-06 is set to 50% or less of its factory default.
• E2-03 = 0
Correct the values set to E2-02, E2-03, or/and E2-06.